Attention sparkies. Shortly after moving into our house 14 years ago I had a company come and install a safety switch in the meter box. This has been tested and works well. My problem now is that I have two fluro lights wired on a two way circuit. Twice in the last couple of days as I switched them off I have blown the safety switch. I was under the impression that this safety switch was monitoring the power circuits, not the light circuits. Both times the switch tripped it plunged the house into darkness but left the power outlets on. I think I have a problem somewhere. I was thinking that maybe the fluro lights pick up power from the power circuit, but if that was the case the safety switch would kill the power circuits, which is not happening. Any suggestions, before the house catches alight?? Jim

Blknight.aus
22nd December 2015, 11:39 AM
the safety switch should be kicking on any discrepencies on the circuit. you could have leakage to earth on the power circuit thats taking out the safety switch.

Id start by basic fault finding turning off all the lighting circuits and working out where the feed for the fluros is actially coming from, the lighting circuit or the power circuits.

if the fluros feed has been taken from the power circuit and thats the only one protected by the safety switch then its possibly a fault in the light itself.

Same same if the lighting ciruit is protected, turn off all the power circuits and then if it still trips most likely the fault is still the light or the switches.

thats all you can do for fault finding at the customer level without opening the box and working out the circuit wiring. In theory there should be a mark up that tells you what circuits are running on the safety switch which will help you work out what is and isnt protected by the safety switch.

It could also be the back feed from the power supply for the fluros depending on which sort they are, what switching and wiring was done to setup the double switching. it could just be "noise" coming out of the fluro on turn off as the capacitors discharge.

bee utey
22nd December 2015, 12:03 PM
I'm going to guess that the fault in the lights circuit is inducing a current surge in an adjacent power cable causing the RCD* to trip out. I remember being surprised in my first house when I tripped a breaker in the shed with a major machine fault, which then caused the house RCD to trip in sympathy. The house was 20m away on an underground feed from the shed which had the meter box on it.

Your fault may be in one of the fluoro lights, try taking one tube out. It may also be in one of the switches if a looping terminal is being used. A separate blue point for the looped cables might help. I had a lights circuit once that would occasionally flash over to the loop when switching a load.

If you can get in your roof space it might pay you to see how closely the power and lights cables are run.

Finally you might have a smaller current surge if you use replacement LED tube in the fittings, they use half the current and don't run through the iron ballast if fitted properly. They're unlikely to surge and light up to full brightness in a flash. :wasntme:

*RCD = residual current device, aka safety switch or earth leakage breaker.