    Fridgie question

    Question for the fridgies, if one was to use this with, say a 2 or 2.5 split system, inverter type condenser unit, would it drop a 2.4x2.4x1.2 cool room to +2 deg.



    Image not available Photos not available for this variation <style type="text/css">.vi-hide-mImgThr {display: none;}</style><img id="icImg" class="img img500" itemprop="image" src="http://i.ebayimg.com/00/s/Mzc1WDUwMA==/z/Fx4AAOxyVaBS6JKj/$_12.JPG" style="" clk="" alt="Unit-Cooler-Evaporator-HEJ-3D-1-7KW-med-temp" />





    Have one to sell? Sell it yourself

    Details about Unit Cooler Evaporator HEJ 3D 1.7KW med temp

  2. #2
    Join Date
    Feb 2012
    Location
    Cleveland
    Posts
    392
    Total Downloaded
    0
    Nup..... The 2.5Kw Split Unit you mentioned is not designed for the suction temps needed........ forget it.... wrong refrigerant most likely as well

  3. #3
    Join Date
    Apr 2008
    Location
    Brisbane,some of the time.
    Posts
    14,186
    Total Downloaded
    0
    A 1.5 to 2.0kw refrigeration unit(at -5 SST) is what you need,as others have said,forget the A/C unit