    Air conditioners

    Can anyone tell me what is the maximum sized split system that can be used on 1 phase power without having problems?

  2. #2
    lokka Guest
    Quote Originally Posted by dobbo
    Can anyone tell me what is the maximum sized split system that can be used on 1 phase power without having problems?
    go buy a fan

  3. #3
    lokka Guest
    Most splits need 15 amps or beta a 3 hp shold run ok on a 15 amp outlet but u mite want to speak to a lecki to be sure

    or u could jst go with my first response much cheaper or move closer to the coast no a/c needed here

    cheers

    chris

  4. #4
    Join Date
    Jan 1970
    Location
    Kyabram, VIC 3620
    Posts
    2,544
    Total Downloaded
    0
    Quote Originally Posted by dobbo
    Can anyone tell me what is the maximum sized split system that can be used on 1 phase power without having problems?
    It depends on if it's an inverter type split or a traditional type

    Traditional about 36,000 btu/hr (or 3 tr) or (10.5 kw)

    Inverter you may get up to 50,000 btu/hr (4.2 tr) or (14.6 kw)

    and before you ask - you cannot measure cooling capacity in horse power

    There are some 'chinese' inverters around which state that you can run 60,000 btu (5 tr) - but I wouldn't be game.

    ..........If you take the maximum size of the fuse/cable normally run in a house/appartment, which is 30 amps

    30 amps x volts (220) = 6600 watts or 6.6 kw - so any unit that has an input power of less than 6 kw (10% margin)
    Last edited by ladas; 8th December 2006 at 09:34 AM.

  5. #5
    Join Date
    Jan 1970
    Location
    Bracken Ridge, Brisbane
    Posts
    1,926
    Total Downloaded
    0
    IT will depend on a few things

    1/ What size are your mains ? ( from the street to your house )

    2/ You will need to do a maximum demand calculation on your house.

    If all this is good then as long as its single phase your main manufacturers will go to 8kws cooling cycle heating is always slightly higher .

    Mitsubishi heavy industries do go higher than 8kw but I am not sure how big they go.

    Rule of thumb to figure out the size A/C you need

    m2 x 150watts = kw

    So measure your square meterage and multiply it by 150 that will give you your total watts required

    eg: 6m x 6m = 36 x 150 = 5400w or 5.4kw

    Hope this helps

  6. #6
    Join Date
    Jan 1970
    Location
    Bracken Ridge, Brisbane
    Posts
    1,926
    Total Downloaded
    0
    Horse power is on older way of A/C sizing

    8kw = 3.5hp

    7.2 kw = 3hp

    5.1kw = 2.5hp

    These are only a rough estimate, but some older A/C installers still refer to HP for sizing.

  7. #7
    Join Date
    Jan 1970
    Location
    Close enough to their Shire to smell the dirty Hobbit feet
    Posts
    8,059
    Total Downloaded
    0
    Thanks for the info guys, now time do do some homework

  8. #8
    Join Date
    Jan 1970
    Location
    Melbourne, Vic
    Posts
    230
    Total Downloaded
    0
    From memory, most houses are supplied about 80A max. Could be 60. Check your main CB.

    So, you can run anything up to 80A theoretically, but you'd probably want things like lights/refrigeration and power elsewhere etc etc... :-)

    So, assume about 25A. That'll get you about a 7 or 8kw unit.

    ***NOTE***
    Rated unit cooling/heating kW or hp does NOT translate directly to electrical kW/hp.

    Gotta read the specs in the manual for peak current draw. Be careful of some of the cheap makes: they may not have 'soft-start' and peak current (at start up) will be significantly higher than rated current draw.
    Current: ‘16 Disco Sport (7seater) aka « Family Bus 2 »
    Sadly Gone: '77 RRC 2 Door aka "Beast"
    Gone: '92 RRC Vogue SE aka "The Family Bus"
    Long Gone: '99 Td5 Defender aka "The TANK!"

  9. #9
    Join Date
    Jan 1970
    Location
    Bathurst NSW
    Posts
    14,445
    Total Downloaded
    0
    Dont most of those sytems need wiring in by an electrician etc anyway? Matt
    <a href=https://the4wdzone.com.au/wp-content/uploads/logo.png target=_blank>https://the4wdzone.com.au/wp-content/uploads/logo.png</a>
    The 4wd Zone/Opposite Lock Bathurst
    263 Stewart Street, Bathurst, NSW
    http://www.the4wdzone.com.au/
    Discounts for AULRO members, just shoot me a PM before you purchase.

  10. #10
    Join Date
    Jan 1970
    Location
    NSW far north coast
    Posts
    17,285
    Total Downloaded
    0
    Daikin have a nominal 9kw single phase inverter split available now. (and a 15.5kw inverter ducted)
    Installed a Saudi Arabian 9kw thing a few years back (Cooline ??) that used a normal AC (non-inverter) compressor. Should've seen the meter spin when that fired up.