    Hint :Cheaper way for install is ask the sparky if he is able to do the refridgerant side aswell as the electrical.

    Normal cost for install subject to variations would be $600app for a back to back install, anything cheaper is a bargin or mates rates

  3. #13
    Join Date
    Jan 1970
    Location
    Brisbane
    Posts
    5,486
    Total Downloaded
    0
    Quote Originally Posted by rick130
    Daikin have a nominal 9kw single phase inverter split available now. (and a 15.5kw inverter ducted)
    Installed a Saudi Arabian 9kw thing a few years back (Cooline ??) that used a normal AC (non-inverter) compressor. Should've seen the meter spin when that fired up.
    We've got a 13.5kw daikin inverter that scales from 4.5 to 14.5 kw. They needed two wires from the mains for it.

  4. #14
    Join Date
    Jul 2006
    Location
    Ringwood VIC
    Posts
    407
    Total Downloaded
    0
    From a sparkies point of view,

    All new houses must have a minimum mains size of 16mm2 which allows for 80Amps, this has definately been the case since 2000 and probably going back to the early 80's. As far as the largest unit goes you will need a sparkie or just the info to calculate out a maximum demand, which if it is over 80A means you will need larger mains, most new/renovated houses in ritzy areas now have 3phase which means you can have 16mm2 mains where as in single phase they would need at least 35mm or higher (which with the price of copper can be expensive).

    Just looking at the book and maximum demand for Airconditioners is 75% of the full load current, so for a 6kw A/C you need to allow 75% of 25 Amps which is 18.75A. This figure has nothing to do with cablesize to the unit, only the house mains.

    Pretty safe to say that if your wiring is fairly new and unless you have a huge house with 5 Bedrooms, spa/sauna and umpteen thousand downlights your mains should be ok.

    Hope that helps, and that i didn't get to nerdy on you. If you have any more Q's I should be able to help.

    Cheers
    Stu

    P.S. If you are getting a sparkie in, it might be worthwhile getting safety switches installed if you don't have them already.