Originally Posted by
mark_coffey
As an industrial maintenance electrician, I have come across this problem a few times. One had been usint this MIG for about 2 years without a problem on the 15A plug, The issue came about when trying to weld continuously for more than 10 minutes on 10mm plus plate over 3m long, the current draw far exceeds the ability of the supply and more importantly the protection device from tripping. Basically the welder will draw what it needs to feed the output.
We have overcome this by fitting out with a standard 32A, welder runs max 30Aish, 5 pin plug and wired for single phase, this allows for use anywhere with standard outlets.
The circuit breakers only use in life is to protect the fixed wiring in in the installation, doesnt matter what you plug in! doesnt care!
If you do have 20A protection and a 15A outlet, I would be more concerned with what sized cable is feeding the outlet and what it is run through, the biggest problem with running high current through cable is the dissapation of the heat, generally only rated to 65degC.
If you are only welding light guage material and in short runs, not a problem, rely on the breaker for your run time and work accordingly, If you do want to be more commercial with your setup, rewire and be safe you wont burn your shed down.